Dear Sir or Madam,I try to communicate by the DeviceNet protocol in using HAL.
In the specification, it is necessary to sample the point of more than 80% for synchronization.
I want to check the CAN bit timing, SS, PTS, PBS1, and PBS2.
How should I do?
Hi Magic,
for CAN or DeviceNET the netX is only able to set the following sample point:
Baud Rate (kBaud) - Sample Point (%)
====================================
1000 - 77
800 - 82
500 - 88
250 - 88
125 - 88
100 - 88
50 - 88
20 - 88
10 - 88
The syncronization rules are observed by the netX.