with Sycon you can only configure connections from originator side on the scanner DTM.
If the adapter functionality of a scanner shall used. The assemblies or the connection have to be configured with the packet API (EIP_OBJECT_AS_REGISTER_REQ). At the originator scanner the connection can be configured by adding a default device.
Andreas Jacob
Hilscher Gesellschaft fuer Systemautomation mbH
Hi Houzenan,
with Sycon you can only configure connections from originator side on the scanner DTM.
If the adapter functionality of a scanner shall used. The assemblies or the connection have to be configured with the packet API (EIP_OBJECT_AS_REGISTER_REQ). At the originator scanner the connection can be configured by adding a default device.
Regards
AJ